What is the recommended tension resistance for variable embedment depth range of Hilti HST3-R
What is the recommended tension resistance for variable embedment depth range of Hilti HST3-R M16 anchors with hef = 120mm; concrete grade C45; in cracked concrete.
2 Replies
Posted by RON SIU23 days ago
Dear Thomas,
Thank you for your enquiry.
Recommended loads are calculated based on the follow assumption:
- A single anchor
- No edge distance and spacing influence
- Min. base material thickness.
As such, the recommended tension load is 17.5kN for HST3-R M16 with hef=120mm.
Please feel free to contact us if you need any further assistance.
Regards,
Ron Siu
Senior Technical Engineer
HILTI(HK)
Posted by THOMAS HAU22 days ago
Dear Ron,
Thank you for kindly reply.
I would like to know how do you calculate the recommended tension resistance with variable embedment depth range.
Because i got a project with 2 different embedment depth, one is 120mm and the others are 100mm.
Best Regards,
Thomas