What is the recommended tension resistance for variable embedment depth range of Hilti HST3-R

Posted by THOMAS HAUabout 2 months ago
What is the recommended tension resistance for variable embedment depth range of Hilti HST3-R

What is the recommended tension resistance for variable embedment depth range of Hilti HST3-R M16 anchors with hef = 120mm; concrete grade C45; in cracked concrete.

recommended,tension,resistance

2 Replies
Posted by RON SIUabout 1 month ago

Dear Thomas,

Thank you for your enquiry.
Recommended loads are calculated based on the follow assumption:

  1. A single anchor
  2. No edge distance and spacing influence
  3. Min. base material thickness.


As such, the recommended tension load is 17.5kN for HST3-R M16 with hef=120mm.
Please feel free to contact us if you need any further assistance.

Regards,
Ron Siu
Senior Technical Engineer
HILTI(HK)


Posted by THOMAS HAUabout 1 month ago

Dear Ron,

Thank you for kindly reply.

I would like to know how do you calculate the recommended tension resistance with variable embedment depth range.

Because i got a project with 2 different embedment depth, one is 120mm and the others are 100mm.

Best Regards,
Thomas