What is the recommended tension resistance for variable embedment depth range of Hilti HST3-R
What is the recommended tension resistance for variable embedment depth range of Hilti HST3-R M16 anchors with hef = 120mm; concrete grade C45; in cracked concrete.
2 Replies
Posted by RON SIUabout 1 month ago
Dear Thomas,
Thank you for your enquiry.
Recommended loads are calculated based on the follow assumption:
- A single anchor
- No edge distance and spacing influence
- Min. base material thickness.
As such, the recommended tension load is 17.5kN for HST3-R M16 with hef=120mm.
Please feel free to contact us if you need any further assistance.
Regards,
Ron Siu
Senior Technical Engineer
HILTI(HK)
Posted by THOMAS HAUabout 1 month ago
Dear Ron,
Thank you for kindly reply.
I would like to know how do you calculate the recommended tension resistance with variable embedment depth range.
Because i got a project with 2 different embedment depth, one is 120mm and the others are 100mm.
Best Regards,
Thomas