Question.1 In submission folder, page 2, do you have hex head for screw?
Question. 2 The panel thk. with attached steel plate is ~20mm, please advise M8x12 or M8x24 is suitable for construction.
Question.3 Can the mentioned anchor bolt be applied 65x45mm in attached block section during the anchor extracted?

anchor bolts,block wall

1 Reply
Posted by Danielover 4 years ago
Hilti Verified

Dear Jacky,

Thank you for your enquiry. Please find the below replies for your reference.

Question 1:
We only have round head for HHD-S light duty metal anchors.


Question 2:
M8*24 is more suitable since the panel thickness for M8*24 is 23-25mm and M8*12 is only 11-13mm. However, it does not meet the 20mm requirement. So, it is suggested that a pull-out test should be carried for the inspection.


Question 3:
HHD-S can be applied on drywall and masonry. So, it should be applicable for your case. However, there are another considerations such as loading requirement and fixture thickness. You may find the details in the submission folder also.

If you would like to have further discussion, please feel free to contact us via email TeamEngineering.HK@hilti.com or at 82288118 for engineering advise.

Thanks,
Daniel
Technical Engineer


1 comment on this reply
Posted by Jackyover 4 years ago
Dear Daniel In the above cavity case (~16mm thk.wall), would you suggest the product, Sleeve anchor HLC-H 10x40/5 #385841 ( for solid wall case) or Cavity anchor HHD-S M8/24x66 #332074 or other anchor for the fixing work? BR Jacky Yeung