Posted by LW LEUNGabout 4 years ago
Hilti PROFIS Engineering 3.0.79

When input forces, do I need to multiply by 2 to suit Hong Kong Building Department's requirement?

anchor design,Profis Engineering

1 Reply
Posted by Lillian Wongabout 4 years ago
Hilti Verified

Hi Mr. Leung,

Thank you for your enquiry.

The Building Department is required safety factor of 3 for the anchor calculation. If your submission is required to submit to Building Department, then you need to apply safety factor of 3 in your calculation.

In our software "Profis Engineering", If you select the FOS 3 in the Design method, it is already including load factor = 2 and material factor = 1.5 in your design. You can directly input the working load after selecting the FOS3 method. (Please find the attachment for details)

Please feel free to contact us if any questions.

Thanks

Best Regards,
Lillian Wong