Load test of anchor bolt HST-3R M16

Posted by THEODORE HUIover 3 years ago
Load test of anchor bolt HST-3R M16

Hi. If the design load is far less than recommended load. Should use 1.5 time design load instead of recommended load for load test?

pull out test,Shear Test

1 Reply
Posted by Hilti Employee (lamder)over 3 years ago

Dear Theodore,
 
Thank you for your enquiry. The test load should be determined by BD/RSE/AP or other authorized parties. However, if we are following the requirement by BD (which is the common practice), the test load should be 1.5 * recommended load instead of the design acting load since its purpose is for verifying the installation quality.
 
Please let me know if there are any questions.
 

Regards,
HILTI (Hong Kong) Limited