Minimum embedment depth of rebar for repairing concrete spalling at non structural wall using Hilti HY200R

Posted by WAH TAT PUNabout 3 years ago
Minimum embedment depth of rebar for repairing concrete spalling at non structural wall using Hilti HY200R

Please advise minimum embedment depth of rebar for repairing concrete spalling at non structural wall using Hilti HY200R

embedment,HY200R,depth

1 Reply
Posted by Danielabout 3 years ago
Hilti Verified

Dear Wah Tat,

Thank you for your enquiry.

Hilti HY200-R with rebar is used as a post-installed rebar system. The minimum embedment of PIR should be referred to the standard EC2 instead of product itself. According to Clause 8.4.4(1), the minimum embedment depth of PIR usually is 10d. Since we are not sure the details of your project, please see if the above is applicable for your case.

Thanks,
Daniel