Skip to main content
Cart

post drill-in rebar test load

Posted by KIN LONG YEUNGabout 2 years ago
post drill-in rebar test load

what is the test load with HY200 with rebar?

Under Building Department Approval Requirement, Is there any test load failure criteria limit to the bar break failure so that the test load is limited to 0.87FyA?

BD approval,TST LAOD

1 Reply
Posted by WILL LIabout 2 years ago
Hilti Verified

Dear Kin Long Yeung,

The purpose of onsite pullout test is verifying the workmanship of the installation, according to the Code of Practice for the Structural Use of Steel 2011, the materials safety factor is 1.15 for rebar. Therefore, the test load should not exceed the 0.87 x yield load of rebar to avoid permanent damage to the rebar.


Kind Regards


Will Li

Technical Engineer