may i know the pull out test sample frequency for HST3 according to BS 5080-1:1993, thanks

hst3,pull out test

1 Reply
Posted by Danielover 3 years ago
Hilti Verified

Hi Hilda,

The actual number of testing sample is subjected to the requirement of BD/RSE/Consultant/AP. From the experience, the sampling rate should be at least 5% or 5 nos, whichever is more, of each type and size of anchors installed. You may confirm with the authorized parties. BS5080 should be referring to the testing procedure.