Skip to main content
Cart

Tensile and shear load test

Posted by Hugo Yeungabout 1 month ago
Tensile and shear load test

In Hong Kong, If the anchor is under tensile and shear force, it is necessary to carry out tensile proof load test and shear proof load test?
If the anchor is under shear force only, it is necessary to carry out tensile proof load test?

proof load,test

1 Reply
Posted by RON SIU29 days ago

Dear Hugo,

Thank you for your enquiry.

In Hong Kong, proof load testing of post-installed anchors is typically carried out in accordance with PNAP APP-169, which requires tensile and/or shear proof load testing depending on the project requirements. The acceptance criteria and the type of proof load test to be conducted should be determined by the Registered Structural Engineer (RSE) or relevant specialist.

As described in PNAP APP-169, the proof load is generally 1.5 times the recommended load. Rather than reproducing the actual design actions, the test tends to be checking quality of the anchor installation.

In our recommendation, tensile proof load test shall adequately review the workmanship of installed anchor disregarding the direction of the actual design force.

Thanks.

Ron Siu
Technical Engineer
HILTI (HK)